POV-Ray : Newsgroups : povray.off-topic : Scientific inquiry Server Time
1 Nov 2026 04:09:16 EST (-0500)
  Scientific inquiry (Message 1 to 11 of 11)
Subject: Scientific inquiry
Date: 11 May 2012 08:24:59
Message: <4fad051b$1@news.povray.org>
Today, ladies and gentlemen, I am performing a scientific experiment.
Yes, I realise how shocking it is that a guy working for a lab company
would actually be doing science. ;-)
It's not exactly the LHC, of course. No, it's rather more mundane than that.
The experiment:
Take one laptop. Place it in the server room for 12 hours. The server
room is kept at an icy 19°C at all times. The huge air conditioning unit
on the wall does that - as well as blowing away any bits of paper not
securely weighted down.
Turn on the laptop, and invoke the diagnostics tool from the BIOS
screen. Abort the testing procedure, and let it just sit there on the PC
health screen.
This screen gives me various readings. Among them are entries entitled
"CPU thermistor", "ambient thermistor" and "SODIMM thermistor". It
appears that the display only updates every 60 seconds, and there is no
way to make it update any faster, which is a pity.
The "experiment" then consists of writing down the numbers displayed and
the wall clock time, until the laptop switches off.
For today's run, the readings are as follows:
   Time | CPU  | Ambient | SODIMM
  12:22 | 41°C |   19°C  |  20°C
  12:23 | 61°C |   21°C  |  25°C
  12:24 | 74°C |   22°C  |  28°C
  12:25 | 83°C |   23°C  |  31°C
  12:26 | 87°C |   24°C  |  33°C
  12:27 | 90°C |   25°C  |  35°C
  12:28 | 93°C |   27°C  |  37°C
  12:29 | 94°C |   27°C  |  38°C
  12:30 | 94°C |   28°C  |  39°C
  12:31 | 95°C |   29°C  |  40°C
  12:51 | 97°C |   36°C  |  47°C
Pro-tip: The temperature in the server room IS NOT 36°C. According to
our officially calibrated laboratory thermometer, it's 18.7°C (± 0.2°C,
for that is the calibration tolerance of this particular instrument). Of
course, I doubt that this "ambient thermistor" is located right on the
outside of the laptop casing.
Eventually the laptop turns off, and when you next turn it on, the BIOS
event log shows a shutdown due to a "critical thermal event". With the
CPU running at nearly the temperature of boiling water, this seems
unsurprising.
Initially the fan isn't spinning at all. By the end of the test, it's
reported as spinning at 5000RPM, which I imagine is its maximum speed.
The really weird thing is this: The laptop doesn't feel hot. At the end
of the last test, the underside was slightly warm. But not warm enough
to boil water on. Similarly, the air being blasted out of the vents at
high speed feels at best very slightly warm.
I gather that air in motion always feels cooler than it really is. But
I've had laptops that you could dry your hands with. For that matter,
I've had laptops that could cook your lap! This laptop isn't ICE cold,
but it's barely what I'd describe as "warm".
So... WTF? o_O
Anyway, I've noticed a couple of times now that the shutdown happens
just as the memory test is running, so I'm going to try again a bit
later and see if I can reliably reproduce this behaviour...
Subject: Re: Scientific inquiry
Date: 11 May 2012 09:54:55
Message: <4fad1a2f@news.povray.org>
> that.
> The experiment:
> health screen.
If you can get a hand on a thermal camera, you might want to observe
that laptop with it.(looking for a hotspot)
Also, have you put the laptop on a wooden table ?
Have you tried leaving it 1 cm above the table (with only two linear
supports underneath, one per side ) ?
The ambient sensors might be on the bottom side, and on a wooden table,
it can rise.
If the exhaust is cool enough, what about the intake ? are they opened
enough ?
Can you run that laptop while opened to see the fan ?
Date: 11 May 2012 10:12:53
Message: <4fad1e65$1@news.povray.org>
I would *love* to be able to play with a thermal camera. 8-)
I spoke to a guy the other day. His job - get this - he gets paid to
look at high-power cutting lasers using a thermal camera. How neat is that?!
> it can rise.
Yeah, first time was on my desk. Second time has balanced on a stack of
books with free air around the edges. I'm not completely sure where the
fan intake is though, it might still have been covered. And of course,
the body of the laptop would have been actually touching the books it
was resting on...
> enough ?
I had to open the case to take the HD out and retrieve some files. I can
see the CPU heat-sink and heat-pipe. All appear to be in order. I can't
see the fan though. None of the visible vent openings look clogged. (The
laptop sits on a desk in a docking station and almost never leaves the
building. So... totally worth buying a laptop then!) I did try blasting
it with some compressed air, but that had no effect.
I might try running it with the case opened, and a temperature probe
pressed against the CPU heat-sink. (Not sure if that will cause
electrical problems though...)
Date: 11 May 2012 11:51:20
Message: <4fad3578@news.povray.org>
It shouldn't, as the heat-sink is attached to the top of the CPU using a
non-conductive adhesive.  If it conducted electricity, that would add to
its heat load (most likely) and cause the temp to go up.
Quite possibly the laptop does not have a thermal sensor that's
calibrated to +/- 0.2C.  It's possible the sensor has failed in some way.
Jim
Date: 22 May 2012 05:37:56
Message: <4fbb5e74@news.povray.org>
OK, so I just signed out our officially certified calibrated laboratory
thermometer and took some measurements.
The ambient temperature on the floor of our server room is 19.6°C. I
wedged the end of the probe into the exhaust vent of the laptop and
fired it up. The highest temperature recorded was 34.7°C. (At this
moment, the laptop was claiming a CPU temperature of 98°C.)
The ambient temperature in our meeting room (which has a nice, large
table) is 22.6°C. I opened up the case and pressed the tip of the probe
against the CPU heat-sink. I'm not 100% sure about how reliable this is.
Before I started the test, the laptop was still warm from the previous
step; I got an initial temperature reading of 25.9°C for the heat-sink,
slowly decreasing as I watched it.
I then fired the laptop up, still balanced on its side, with the exhaust
vent facing upward. The reading quickly rose to about 53°C, and then
wavered up and down from their. Sometimes it fell as low as 52°C,
sometimes it reached as much as 55.5°C. And all the time, the laptop
claims the CPU is at between 92°C and 98°C.
I did find that if I wedge the probe into a certain spot, I could get
the reading to go up as high as 62.8°C.
So, what do we think, folks? Is pressing the tip of a long metal probe
against a metal heat-sink a reliable way to get a temperature reading?
Is it really likely that the CPU could be at almost 100°C while the
surface of its heat-sink is at only 60°C or so? Is it normal for a
laptop heat-sink to get that hot? Should the exhaust be hotter than 35°C
when the heat-sink is so warm? Will Dell give a damn?
Actually, scrub that last one - I already know the answer...
Date: 22 May 2012 07:19:42
Message: <4fbb764e@news.povray.org>
I would use a thermocouple attached to the heatsink with thermal paste.
Once you have done that box the laptop up as the efficiency of its
cooling system will depend on the air flow.
BTW what is your calibrated laboratory thermometer which is a long metal
probe?
Regards
Date: 22 May 2012 07:54:30
Message: <4fbb7e76$1@news.povray.org>
Yeah, I don't have any thermal paste.
Well, that's why I tried it in our server room. The AC holds the room at
a constant temperature. That's also why I used the meeting room; it's
large enough that the presence of one warm human and one hot laptop is
unlikely to affect the overall temperature of such a huge volume of air
with free circulation.
> probe?
It's made be Hanna Instruments (no, I don't know the exact model number)
and I'm using a type-K thermocouple. It was last externally calibrated
by a certified engineer about 8 months ago.
Unfortunately, as I say, the probe for the thermocouple is very long and
thin. It would probably work great for measuring the temperature of the
air in a room, or of a flask of liquid. (That's probably what the lab
guys want it for.) I'm not sure how appropriate it is for measuring the
surface temperature of a solid object.
For reference, I pressed the tip to my leg, and got a reading of about
33°C - not implausible for the outside temperature of a warm-blooded animal.
Date: 22 May 2012 08:35:26
Message: <4fbb880e$1@news.povray.org>
You need some of these:
http://www.eurodidact.co.uk/images/nicrni-01.jpg
That's what we use, you can then just glue or tape several of them onto
whatever you want to log (and leave 1 or 2 dangling around for the air
temperature).
A delta of 35°C between the CPU and heatsink surface might be plausible,
although it entirely depends on how much heat the CPU is dissipating.
If it's dissipating 35W of heat, that gives a thermal resistance of
1°C/W which sounds about right.  I woudl have thought the exhaust would
be hotter than 35°C, but if you're doing all this with the lid off then
that's probably affecting the exhaust temperature significantly.
Besides, isn't your job to send it back to Dell when it's broken, not
try and repair it yourself?
Date: 22 May 2012 11:10:04
Message: <4fbbac4c@news.povray.org>
> temperature).
Hmm, yes, that looks far more suitable.
> although it entirely depends on how much heat the CPU is dissipating. If
> it's dissipating 35W of heat, that gives a thermal resistance of 1°C/W
> which sounds about right. I woudl have thought the exhaust would be
The exhaust measurements were taken with the laptop fully assembled, and
placed in a normal operating position. (I.e., resting on a flat surface.
I note the air intake is on the underside. Since it was resting on a
/hard/ surface, it should still be getting good intake.) This was also
in a server room held at a chilly 19°C.
The CPU heat-sink measurements were taken in a room a few degrees
warmer, obviously with the case off, and with the laptop resting on its
side with the exhaust vent upwards. I'm sure that's not a configuration
the manufacturers will be expecting you to try.
Yeah, but then I'd have to talk to that Asian guy who doesn't speak
English...
Basically I want to determine whether the hardware is actually doing
something abnormal before I send it back. Although running the fan
constantly and reporting a CPU temperature of nearly 100°C when the
laptop isn't even DOING anything sounds fairly abnormal to me...
Date: 22 May 2012 11:30:31
Message: <4fbbb117$1@news.povray.org>
IME (which might be out of date by now) the BIOS does actually use 100%
CPU.  I guess it just never puts the CPU to sleep, and loops waiting for
a keypress.
Have you checked the heatsink is properly attached to the CPU?  That
would be my guess.
Date: 22 May 2012 11:47:29
Message: <4fbbb511$1@news.povray.org>
> a keypress.
Yeah, I've seen various DOS and BIOS programs that use busy-waiting
rather than suspending the CPU. So that /might/ be the cause.
OTOH, under Windows the fan quickly ramps up to maximum speed also. This
suggests to me that the problem is simply that the CPU is overheating.
> would be my guess.
The purpose of all the measuring was to determine whether the fault is
the temperature sensors reporting an erroneously high temperature, or
the cooling system failing to cool the CPU.
The heat-sink /looks/ to be attached securely enough. There is also
nothing obviously wrong with the heat pipe or the fans. It's quite a new
laptop, and I can't see any sign of dust build-in in the air vents. It's
all quite puzzling...